Jim Sanford wrote:
The situation you describe regarding load sharing between multiple
parallel sources, without oscillations and circulating currents, is no
different than the situation where there are multiple AC generators
operating in parallel. In that case, the speed governor (which sets
frequency) has a frequency vs load characteristic that is not flat.
This forces stable real load sharing, even when generators of different
capacity are paralleled. Similarly, the voltage regulator has a
non-flat voltage vs. reactive load characteristic. This forces stable
sharing of reactive load.
I'm not sure this is the exact same situation. A generator is not a
stored energy device (ignoring flywheel effects). It can't produce more
electrical power out than the mechanical power going in. A battery or
cap, on the other hand, can produce almost arbitrarily large powers
until it is depleted.
I agree, this is all manageable.
My thoughts on this comes from experience with related problems in home
photovoltaic power systems.
In the late 1990s, the Trace SW4048/5548 inverter models were very
popular. These 4/5.5 kVA inverters are bidirectional; power can flow
from the AC side to the 48V DC side as well as from the DC side to the
AC side. This is useful in maintaining a battery bank at a constant
voltage despite varying PV production and DC load, but it also led to
problems in systems with more than one unit.
Two inverters are commonly used in larger (e.g., 5kW) grid-tied systems.
They were typically wired in parallel on the DC side and connected to
opposite 120V phases on the AC side.
Even if you set both inverters to the same "sell" voltage on their DC
side, small differences in their internal voltage references often
result in very different inverter power levels. You could even see one
inverter "buying" (converting AC to DC) while the other "sold"
(converting DC to AC), obviously a wasteful situation. This problem
could have been easily avoided with a small dead band around the DC
operating setpoint. This could also shut down the inverter at night,
avoiding its idle power consumption.
Another problem comes from the use of a PV charge controller with this
inverter. In a grid tied PV system, the charge controller is basically a
safety device that protects the battery against an inverter or grid
failure. Normally you always want maximum power from the PV array
because the grid is an infinite energy sink and we can sell whatever we
produce. During an outage or failure, though, we have to back off PV
production to match local consumption. It does this whenever the battery
bus voltage rises above a set point.
But the inverter is also trying to control the DC bus voltage. If you
don't set them both up carefully, the charge controller could shut down
the array unnecessarily. Again, an inverter dead band would have been
very useful.
The bottom line is that all the devices on the DC bus must somehow
coordinate their operation. If they communicate implicitly through DC
bus voltage, then they need to agree on just what is meant by every
possible value of bus voltage.
--Phil